There are different breakers available. The typical breaker is a magnetic/thermal breaker. It'll trip at whatever its rating is (IIRC, 50ms for most).
An example is Eaton's time chart.
https://www.eaton.com/content/dam/e...elboards/br-family-trip-curves-tc003002en.pdf
As a heads up, if the saw starting is tripping the circuit, try replacing the breaker. NOT with a higher rated breaker, same name plate rating. A worn breaker typically reduces its trip time. That is a good place to start.
But as you can see from their chart, you are talking about 30ms trip time at 600-1500% current (short circuit). You are talking around a minute of capacity at 200-300% current. Now if the saw has a short in the windings, it is possible the inrush current is greater than this range, but you should still have several seconds of load capacity even at the top end of this range on the breaker.
The short version is, there is a problem in the saw, or it is a worn breaker. Or the circuit is being run near max already. Even at 400% of rating, you've got around 5-6s as the minimum trip time.
Eaton's figures are pretty similar to Siemens and other magneto-thermal circuit breakers from my experience.